Hi guys,

Just installed one SmartAPC (Dell model) - DLA1500RM2U

The UPS is using USB to one ESXi host and the "debian" is a VM on thast host.
Everything went very smooth, but I'm receiving some weird data:
APC      : 001,042,1001
DATE     : 2016-10-22 22:44:26 -0400  
HOSTNAME : debian
VERSION  : 3.14.10 (13 September 2011) debian
UPSNAME  : DLA1500RM2U
CABLE    : USB Cable
DRIVER   : USB UPS Driver
UPSMODE  : Stand Alone
STARTTIME: 2016-10-22 20:52:14 -0400  
MODEL    : 
STATUS   : ONLINE 
LINEV    : 000.0 Volts
LOADPCT  :   0.0 Percent Load Capacity
BCHARGE  : 100.0 Percent
TIMELEFT :  28.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
OUTPUTV  : 000.0 Volts
SENSE    : High
DWAKE    : -01 Seconds
DSHUTD   : 090 Seconds
LOTRANS  : 106.0 Volts
HITRANS  : 127.0 Volts
RETPCT   : 000.0 Percent
ITEMP    : -273.1 C Internal
ALARMDEL : 30 seconds
BATTV    : 00.0 Volts
LINEFREQ : 0.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT  : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI   : 14 days
STATFLAG : 0x07000008 Status Flag
MANDATE  : 1980-00-00
SERIALNO : 
BATTDATE : 2008-12-18
NOMOUTV  : 120 Volts
NOMBATTV :   0.0 Volts
END APC  : 2016-10-22 22:44:29 -0400  
Wasn't sure if the problem is in the only initially installed Windows monitor, but after that the verification from the Linux console and from all the additional GUI were the same.

Is that well-known issue or it's something new?
I was searching the list, but didn't found any similar post...

Thank you for the great tool anyway,

Alex




------------------------------------------------------------------------------
Check out the vibrant tech community on one of the world's most
engaging tech sites, SlashDot.org! http://sdm.link/slashdot
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users
Reply | Threaded
Open this post in threaded view
|  
Report Content as Inappropriate

Re: Fwd:

Ted Mittelstaedt-5

Are you using MODBUS, of this is a Dell-modified APC UPS that is
fairly new you have to talk to it with MODBUS protocol not the
older Smartlink protocol.  Look in the manual to set that up.

Ted


On 10/24/2016 5:36 AM, Aleksandar Aleksiev wrote:

> [hidden email]
> <mailto:[hidden email]>
>
>
> Hi guys,
>
> Just installed one SmartAPC (Dell model) - DLA1500RM2U
>
> The UPS is using USB to one ESXi host and the "debian" is a VM on thast
> host.
> Everything went very smooth, but I'm receiving some weird data:
>
> APC      : 001,042,1001
> DATE     : 2016-10-22 22:44:26 -0400
> HOSTNAME : debian
> VERSION  : 3.14.10 (13 September 2011) debian
> UPSNAME  : DLA1500RM2U
> CABLE    : USB Cable
> DRIVER   : USB UPS Driver
> UPSMODE  : Stand Alone
> STARTTIME: 2016-10-22 20:52:14 -0400
> MODEL    :
> STATUS   : ONLINE
> LINEV    : 000.0 Volts
> LOADPCT  :   0.0 Percent Load Capacity
> BCHARGE  : 100.0 Percent
> TIMELEFT :  28.0 Minutes
> MBATTCHG : 5 Percent
> MINTIMEL : 3 Minutes
> MAXTIME  : 0 Seconds
> OUTPUTV  : 000.0 Volts
> SENSE    : High
> DWAKE    : -01 Seconds
> DSHUTD   : 090 Seconds
> LOTRANS  : 106.0 Volts
> HITRANS  : 127.0 Volts
> RETPCT   : 000.0 Percent
> ITEMP    : -273.1 C Internal
> ALARMDEL : 30 seconds
> BATTV    : 00.0 Volts
> LINEFREQ : 0.0 Hz
> LASTXFER : No transfers since turnon
> NUMXFERS : 0
> TONBATT  : 0 seconds
> CUMONBATT: 0 seconds
> XOFFBATT : N/A
> SELFTEST : NO
> STESTI   : 14 days
> STATFLAG : 0x07000008 Status Flag
> MANDATE  : 1980-00-00
> SERIALNO :
> BATTDATE : 2008-12-18
> NOMOUTV  : 120 Volts
> NOMBATTV :   0.0 Volts
> END APC  : 2016-10-22 22:44:29 -0400
>
> Wasn't sure if the problem is in the only initially installed Windows
> monitor, but after that the verification from the Linux console and from
> all the additional GUI were the same.
>
> Is that well-known issue or it's something new?
> I was searching the list, but didn't found any similar post...
>
> Thank you for the great tool anyway,
>
> Alex
>
>
>
>
>
> ------------------------------------------------------------------------------
> Check out the vibrant tech community on one of the world's most
> engaging tech sites, SlashDot.org! http://sdm.link/slashdot
>
>
>
> _______________________________________________
> Apcupsd-users mailing list
> [hidden email]
> https://lists.sourceforge.net/lists/listinfo/apcupsd-users
>


------------------------------------------------------------------------------
The Command Line: Reinvented for Modern Developers
Did the resurgence of CLI tooling catch you by surprise?
Reconnect with the command line and become more productive.
Learn the new .NET and ASP.NET CLI. Get your free copy!
http://sdm.link/telerik
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users
Reply | Threaded
Open this post in threaded view
|  
Report Content as Inappropriate

Re: Fwd:

Aleksandar Aleksiev
Hi Ted!

Thank you for your reply!
It's a pretty old APC model actually - even out of sell, AFAIK...

Just gave it a try with NUT and seems to read everything fine:
~# upsc apc@localhost
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2008/12/18
battery.runtime: 1680
battery.runtime.low: 120
battery.temperature: 21.6
battery.type: PbAc
battery.voltage: 27.7
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1500 RM
device.serial: AS0851230125
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.vendorid: 051d
driver.version: 2.6.4
driver.version.data: APC HID 0.95
driver.version.internal: 0.37
input.sensitivity: high
input.transfer.high: 127
input.transfer.low: 106
input.voltage: 114.4
output.current: 1.41
output.frequency: 60.5
output.voltage: 114.4
output.voltage.nominal: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 667.18.D
ups.firmware.aux: 7.3
ups.load: 15.6
ups.mfr: American Power Conversion
ups.mfr.date: 2008/12/18
ups.model: Smart-UPS 1500 RM
ups.productid: 0002
ups.serial: AS0851230125
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d
~#

Greets,

Alex

2016-10-26 4:53 GMT-04:00 Ted Mittelstaedt <[hidden email]>:

Are you using MODBUS, of this is a Dell-modified APC UPS that is
fairly new you have to talk to it with MODBUS protocol not the
older Smartlink protocol.  Look in the manual to set that up.

Ted


On 10/24/2016 5:36 AM, Aleksandar Aleksiev wrote:
> [hidden email]
> <mailto:[hidden email]>
>
>
> Hi guys,
>
> Just installed one SmartAPC (Dell model) - DLA1500RM2U
>
> The UPS is using USB to one ESXi host and the "debian" is a VM on thast
> host.
> Everything went very smooth, but I'm receiving some weird data:
>
> APC      : 001,042,1001
> DATE     : 2016-10-22 22:44:26 -0400
> HOSTNAME : debian
> VERSION  : 3.14.10 (13 September 2011) debian
> UPSNAME  : DLA1500RM2U
> CABLE    : USB Cable
> DRIVER   : USB UPS Driver
> UPSMODE  : Stand Alone
> STARTTIME: 2016-10-22 20:52:14 -0400
> MODEL    :
> STATUS   : ONLINE
> LINEV    : 000.0 Volts
> LOADPCT  :   0.0 Percent Load Capacity
> BCHARGE  : 100.0 Percent
> TIMELEFT :  28.0 Minutes
> MBATTCHG : 5 Percent
> MINTIMEL : 3 Minutes
> MAXTIME  : 0 Seconds
> OUTPUTV  : 000.0 Volts
> SENSE    : High
> DWAKE    : -01 Seconds
> DSHUTD   : 090 Seconds
> LOTRANS  : 106.0 Volts
> HITRANS  : 127.0 Volts
> RETPCT   : 000.0 Percent
> ITEMP    : -273.1 C Internal
> ALARMDEL : 30 seconds
> BATTV    : 00.0 Volts
> LINEFREQ : 0.0 Hz
> LASTXFER : No transfers since turnon
> NUMXFERS : 0
> TONBATT  : 0 seconds
> CUMONBATT: 0 seconds
> XOFFBATT : N/A
> SELFTEST : NO
> STESTI   : 14 days
> STATFLAG : 0x07000008 Status Flag
> MANDATE  : 1980-00-00
> SERIALNO :
> BATTDATE : 2008-12-18
> NOMOUTV  : 120 Volts
> NOMBATTV :   0.0 Volts
> END APC  : 2016-10-22 22:44:29 -0400
>
> Wasn't sure if the problem is in the only initially installed Windows
> monitor, but after that the verification from the Linux console and from
> all the additional GUI were the same.
>
> Is that well-known issue or it's something new?
> I was searching the list, but didn't found any similar post...
>
> Thank you for the great tool anyway,
>
> Alex
>
>
>
>
>
> ------------------------------------------------------------------------------
> Check out the vibrant tech community on one of the world's most
> engaging tech sites, SlashDot.org! http://sdm.link/slashdot
>
>
>
> _______________________________________________
> Apcupsd-users mailing list
> [hidden email]
> https://lists.sourceforge.net/lists/listinfo/apcupsd-users
>


------------------------------------------------------------------------------
The Command Line: Reinvented for Modern Developers
Did the resurgence of CLI tooling catch you by surprise?
Reconnect with the command line and become more productive.
Learn the new .NET and ASP.NET CLI. Get your free copy!
http://sdm.link/telerik
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users


------------------------------------------------------------------------------
The Command Line: Reinvented for Modern Developers
Did the resurgence of CLI tooling catch you by surprise?
Reconnect with the command line and become more productive.
Learn the new .NET and ASP.NET CLI. Get your free copy!
http://sdm.link/telerik
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users
Loading...