Unable to connect to UPS Network Management Card2 from CentOS

classic Classic list List threaded Threaded
4 messages Options
Reply | Threaded
Open this post in threaded view
|  
Report Content as Inappropriate

Unable to connect to UPS Network Management Card2 from CentOS

yallaone (Bugzilla)
Hello,

I run apcupsd 3.14.10 (13 September 2011) on CentOS release 6.5 (Final), and I have an APC Smart-UPS with a Network Management Card 2 (AP9631).

When trying to get apcupsd to connect over ethernet to the management card, I get an error that it is unable to bind to the socket:

Apr 17 18:48:53 Linux apcupsd[9702]: apcupsd FATAL ERROR in pcnet.c at line 661#012Cannot bind socket (13)

I have verified that there are no other instances of apcupsd runnning, and also no other services claiming that port. The firewall on the Linux-box has been shut down, and I have only one simple switch between the server and the management card. Accessing the management card of the UPS via Web and SSH works fine and the system appears correctly configured. The documentation refers to an earlier version of the management card, but AP9631 is supposedly fully backwards compatible, and regardless of that it seems the error is on the linux box, long before it reaches the card.

I would be very grateful if someone could kindly help me point out what I have missed in order to make this work. Thank you!

grep -v "^#" apcupsd.conf |egrep -v "^\s*$"

UPSNAME SmartUPS

UPSCABLE ether

UPSTYPE pcnet

DEVICE 192.168.1.4:xxxxx:xxxx <-intentionally changed

LOCKFILE /var/lock

SCRIPTDIR /etc/apcupsd

PWRFAILDIR /etc/apcupsd

NOLOGINDIR /etc

ONBATTERYDELAY 6

BATTERYLEVEL 5

MINUTES 3

TIMEOUT 0

ANNOY 300

ANNOYDELAY 60

NOLOGON disable

KILLDELAY 0

NETSERVER on

NISIP 0.0.0.0

NISPORT 3551

EVENTSFILE /var/log/apcupsd.events

EVENTSFILEMAX 10

UPSCLASS standalone

UPSMODE disable

STATTIME 0

STATFILE /var/log/apcupsd.status

LOGSTATS off

DATATIME 0


------------------------------------------------------------------------------
Learn Graph Databases - Download FREE O'Reilly Book
"Graph Databases" is the definitive new guide to graph databases and their
applications. Written by three acclaimed leaders in the field,
this first edition is now available. Download your free book today!
http://p.sf.net/sfu/NeoTech
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users
Reply | Threaded
Open this post in threaded view
|  
Report Content as Inappropriate

Re: Unable to connect to UPS Network Management Card2from CentOS

Seth Bardash
We are running a Symmetra 16000 with a network card. Not sure which version....
I am running CentOS 6.5 x86_64.
 
My apcupsd.conf file looks like this:
 
## apcupsd.conf v1.1 ##
#
#  for apcupsd release 3.14.10 (13 September 2011) - redhat
#
# "apcupsd" POSIX config file
 
#
# ========= General configuration parameters ============
#
 
# UPSNAME xxx
#   Use this to give your UPS a name in log files and such. This
#   is particulary useful if you have multiple UPSes. This does not
#   set the EEPROM. It should be 8 characters or less.
UPSNAME 16KVA
 
# UPSCABLE <cable>
#   Defines the type of cable connecting the UPS to your computer.
#
#   Possible generic choices for <cable> are:
#     simple, smart, ether, usb
#
#   Or a specific cable model number may be used:
#     940-0119A, 940-0127A, 940-0128A, 940-0020B,
#     940-0020C, 940-0023A, 940-0024B, 940-0024C,
#     940-1524C, 940-0024G, 940-0095A, 940-0095B,
#     940-0095C, M-04-02-2000
#
UPSCABLE ether
 
# To get apcupsd to work, in addition to defining the cable
# above, you must also define a UPSTYPE, which corresponds to
# the type of UPS you have (see the Description for more details).
# You must also specify a DEVICE, sometimes referred to as a port.
# For USB UPSes, please leave the DEVICE directive blank. For
# other UPS types, you must specify an appropriate port or address.
#
# UPSTYPE   DEVICE           Description
# apcsmart  /dev/tty**       Newer serial character device, appropriate for
#                            SmartUPS models using a serial cable (not USB).
#
# usb       <BLANK>          Most new UPSes are USB. A blank DEVICE
#                            setting enables autodetection, which is
#                            the best choice for most installations.
#
# net       hostname:port    Network link to a master apcupsd through apcupsd's
#                            Network Information Server. This is used if the
#                            UPS powering your computer is connected to a
#                            different computer for monitoring.
#
# snmp      hostname:port:vendor:community
#                            SNMP network link to an SNMP-enabled UPS device.
#                            Hostname is the ip address or hostname of the UPS
#                            on the network. Vendor can be can be "APC" or
#                            "APC_NOTRAP". "APC_NOTRAP" will disable SNMP trap
#                            catching; you usually want "APC". Port is usually
#                            161. Community is usually "private".
#
# netsnmp   hostname:port:vendor:community
#                            OBSOLETE
#                            Same as SNMP above but requires use of the
#                            net-snmp library. Unless you have a specific need
#                            for this old driver, you should use 'snmp' instead.
#
# dumb      /dev/tty**       Old serial character device for use with
#                            simple-signaling UPSes.
#
# pcnet     ipaddr:username:passphrase:port
#                            PowerChute Network Shutdown protocol which can be
#                            used as an alternative to SNMP with the AP9617
#                            family of smart slot cards. ipaddr is the IP
#                            address of the UPS management card. username and
#                            passphrase are the credentials for which the card
#                            has been configured. port is the port number on
#                            which to listen for messages from the UPS, normally
#                            3052. If this parameter is empty or missing, the
#                            default of 3052 will be used.
#
UPSTYPE snmp
DEVICE 192.168.2.XXX:161:APC:public
 
The rest is pretty much standard and this works fine.
 
After I run service apcupsd start I can access it like this:
 
[root@D6328-10 /]# apcaccess status
APC      : 001,050,1192           
DATE     : 2014-04-17 12:33:51 -0600 
HOSTNAME : D6328-10                  
VERSION  : 3.14.10 (13 September 2011) redhat
UPSNAME  : SYM16K                           
CABLE    : Ethernet Link                    
DRIVER   : SNMP UPS Driver                  
UPSMODE  : Stand Alone
STARTTIME: 2014-04-17 12:32:50 -0600
MODEL    : Symmetra 16000
STATUS   : ONLINE
LINEV    : 242.0 Volts
LOADPCT  :  12.0 Percent Load Capacity
BCHARGE  : 100.0 Percent
TIMELEFT : 199.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
MAXLINEV : 242.0 Volts
MINLINEV : 242.0 Volts
OUTPUTV  : 244.0 Volts
SENSE    : Auto Adjust
DWAKE    : 000 Seconds
DSHUTD   : 020 Seconds
DLOWBATT : 02 Minutes
LOTRANS  : 155.0 Volts
HITRANS  : 276.0 Volts
RETPCT   : 015.0 Percent
ITEMP    : 30.0 C Internal
ALARMDEL : No alarm
BATTV    : 136.0 Volts
LINEFREQ : 60.0 Hz
LASTXFER : Automatic or explicit self test
NUMXFERS : 0
TONBATT  : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : OK
STESTI   : 336
STATFLAG : 0x07000008 Status Flag
MANDATE  : 02/19/04
SERIALNO : ED0408000371
BATTDATE : 12/00/12
NOMOUTV  : 240 Volts
NOMBATTV : 120.0 Volts
HUMIDITY :   0.0 Percent
AMBTEMP  :   0.0 C
EXTBATTS : 13
BADBATTS : 0
FIRMWARE : 260.137.I
END APC  : 2014-04-17 12:34:20 -0600
Hope this helps.....

Seth Bardash

Integrated Solutions and Systems
1510 Old North Gate Road
Colorado Springs, CO 80921

719-495-5866 Shop
719-495-5870 Fax
719-337-4779 Cell

http://www.integratedsolutions.org

Failure can not cope with knowledge and perseverance!

 


From: Halim Issa [mailto:[hidden email]]
Sent: Thursday, April 17, 2014 10:56 AM
To: [hidden email]
Subject: [Apcupsd-users] Unable to connect to UPS Network Management Card2from CentOS

Hello,

I run apcupsd 3.14.10 (13 September 2011) on CentOS release 6.5 (Final), and I have an APC Smart-UPS with a Network Management Card 2 (AP9631).

When trying to get apcupsd to connect over ethernet to the management card, I get an error that it is unable to bind to the socket:

Apr 17 18:48:53 Linux apcupsd[9702]: apcupsd FATAL ERROR in pcnet.c at line 661#012Cannot bind socket (13)

I have verified that there are no other instances of apcupsd runnning, and also no other services claiming that port. The firewall on the Linux-box has been shut down, and I have only one simple switch between the server and the management card. Accessing the management card of the UPS via Web and SSH works fine and the system appears correctly configured. The documentation refers to an earlier version of the management card, but AP9631 is supposedly fully backwards compatible, and regardless of that it seems the error is on the linux box, long before it reaches the card.

I would be very grateful if someone could kindly help me point out what I have missed in order to make this work. Thank you!

grep -v "^#" apcupsd.conf |egrep -v "^\s*$"

UPSNAME SmartUPS

UPSCABLE ether

UPSTYPE pcnet

DEVICE 192.168.1.4:xxxxx:xxxx <-intentionally changed

LOCKFILE /var/lock

SCRIPTDIR /etc/apcupsd

PWRFAILDIR /etc/apcupsd

NOLOGINDIR /etc

ONBATTERYDELAY 6

BATTERYLEVEL 5

MINUTES 3

TIMEOUT 0

ANNOY 300

ANNOYDELAY 60

NOLOGON disable

KILLDELAY 0

NETSERVER on

NISIP 0.0.0.0

NISPORT 3551

EVENTSFILE /var/log/apcupsd.events

EVENTSFILEMAX 10

UPSCLASS standalone

UPSMODE disable

STATTIME 0

STATFILE /var/log/apcupsd.status

LOGSTATS off

DATATIME 0


------------------------------------------------------------------------------
Learn Graph Databases - Download FREE O'Reilly Book
"Graph Databases" is the definitive new guide to graph databases and their
applications. Written by three acclaimed leaders in the field,
this first edition is now available. Download your free book today!
http://p.sf.net/sfu/NeoTech
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users
Reply | Threaded
Open this post in threaded view
|  
Report Content as Inappropriate

Re: Unable to connect to UPS Network Management Card2from CentOS

yallaone (Bugzilla)
Thanks much! Switching to SNMP worked miracles! Much appreciated



On 17 April 2014 20:42, Seth Bardash <[hidden email]> wrote:
We are running a Symmetra 16000 with a network card. Not sure which version....
I am running CentOS 6.5 x86_64.
 
My apcupsd.conf file looks like this:
 
## apcupsd.conf v1.1 ##
#
#  for apcupsd release 3.14.10 (13 September 2011) - redhat
#
# "apcupsd" POSIX config file
 
#
# ========= General configuration parameters ============
#
 
# UPSNAME xxx
#   Use this to give your UPS a name in log files and such. This
#   is particulary useful if you have multiple UPSes. This does not
#   set the EEPROM. It should be 8 characters or less.
UPSNAME 16KVA
 
# UPSCABLE <cable>
#   Defines the type of cable connecting the UPS to your computer.
#
#   Possible generic choices for <cable> are:
#     simple, smart, ether, usb
#
#   Or a specific cable model number may be used:
#     940-0119A, 940-0127A, 940-0128A, 940-0020B,
#     940-0020C, 940-0023A, 940-0024B, 940-0024C,
#     940-1524C, 940-0024G, 940-0095A, 940-0095B,
#     940-0095C, M-04-02-2000
#
UPSCABLE ether
 
# To get apcupsd to work, in addition to defining the cable
# above, you must also define a UPSTYPE, which corresponds to
# the type of UPS you have (see the Description for more details).
# You must also specify a DEVICE, sometimes referred to as a port.
# For USB UPSes, please leave the DEVICE directive blank. For
# other UPS types, you must specify an appropriate port or address.
#
# UPSTYPE   DEVICE           Description
# apcsmart  /dev/tty**       Newer serial character device, appropriate for
#                            SmartUPS models using a serial cable (not USB).
#
# usb       <BLANK>          Most new UPSes are USB. A blank DEVICE
#                            setting enables autodetection, which is
#                            the best choice for most installations.
#
# net       hostname:port    Network link to a master apcupsd through apcupsd's
#                            Network Information Server. This is used if the
#                            UPS powering your computer is connected to a
#                            different computer for monitoring.
#
# snmp      hostname:port:vendor:community
#                            SNMP network link to an SNMP-enabled UPS device.
#                            Hostname is the ip address or hostname of the UPS
#                            on the network. Vendor can be can be "APC" or
#                            "APC_NOTRAP". "APC_NOTRAP" will disable SNMP trap
#                            catching; you usually want "APC". Port is usually
#                            161. Community is usually "private".
#
# netsnmp   hostname:port:vendor:community
#                            OBSOLETE
#                            Same as SNMP above but requires use of the
#                            net-snmp library. Unless you have a specific need
#                            for this old driver, you should use 'snmp' instead.
#
# dumb      /dev/tty**       Old serial character device for use with
#                            simple-signaling UPSes.
#
# pcnet     ipaddr:username:passphrase:port
#                            PowerChute Network Shutdown protocol which can be
#                            used as an alternative to SNMP with the AP9617
#                            family of smart slot cards. ipaddr is the IP
#                            address of the UPS management card. username and
#                            passphrase are the credentials for which the card
#                            has been configured. port is the port number on
#                            which to listen for messages from the UPS, normally
#                            3052. If this parameter is empty or missing, the
#                            default of 3052 will be used.
#
UPSTYPE snmp
DEVICE 192.168.2.XXX:161:APC:public
 
The rest is pretty much standard and this works fine.
 
After I run service apcupsd start I can access it like this:
 
[root@D6328-10 /]# apcaccess status
APC      : 001,050,1192           
DATE     : 2014-04-17 12:33:51 -0600 
HOSTNAME : D6328-10                  
VERSION  : 3.14.10 (13 September 2011) redhat
UPSNAME  : SYM16K                           
CABLE    : Ethernet Link                    
DRIVER   : SNMP UPS Driver                  
UPSMODE  : Stand Alone
STARTTIME: 2014-04-17 12:32:50 -0600
MODEL    : Symmetra 16000
STATUS   : ONLINE
LINEV    : 242.0 Volts
LOADPCT  :  12.0 Percent Load Capacity
BCHARGE  : 100.0 Percent
TIMELEFT : 199.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
MAXLINEV : 242.0 Volts
MINLINEV : 242.0 Volts
OUTPUTV  : 244.0 Volts
SENSE    : Auto Adjust
DWAKE    : 000 Seconds
DSHUTD   : 020 Seconds
DLOWBATT : 02 Minutes
LOTRANS  : 155.0 Volts
HITRANS  : 276.0 Volts
RETPCT   : 015.0 Percent
ITEMP    : 30.0 C Internal
ALARMDEL : No alarm
BATTV    : 136.0 Volts
LINEFREQ : 60.0 Hz
LASTXFER : Automatic or explicit self test
NUMXFERS : 0
TONBATT  : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : OK
STESTI   : 336
STATFLAG : 0x07000008 Status Flag
MANDATE  : 02/19/04
SERIALNO : ED0408000371
BATTDATE : 12/00/12
NOMOUTV  : 240 Volts
NOMBATTV : 120.0 Volts
HUMIDITY :   0.0 Percent
AMBTEMP  :   0.0 C
EXTBATTS : 13
BADBATTS : 0
FIRMWARE : 260.137.I
END APC  : 2014-04-17 12:34:20 -0600
Hope this helps.....

Seth Bardash

Integrated Solutions and Systems
1510 Old North Gate Road
Colorado Springs, CO 80921

719-495-5866 Shop
719-495-5870 Fax
719-337-4779 Cell

http://www.integratedsolutions.org

Failure can not cope with knowledge and perseverance!

 


From: Halim Issa [mailto:[hidden email]]
Sent: Thursday, April 17, 2014 10:56 AM
To: [hidden email]
Subject: [Apcupsd-users] Unable to connect to UPS Network Management Card2from CentOS

Hello,

I run apcupsd 3.14.10 (13 September 2011) on CentOS release 6.5 (Final), and I have an APC Smart-UPS with a Network Management Card 2 (AP9631).

When trying to get apcupsd to connect over ethernet to the management card, I get an error that it is unable to bind to the socket:

Apr 17 18:48:53 Linux apcupsd[9702]: apcupsd FATAL ERROR in pcnet.c at line 661#012Cannot bind socket (13)

I have verified that there are no other instances of apcupsd runnning, and also no other services claiming that port. The firewall on the Linux-box has been shut down, and I have only one simple switch between the server and the management card. Accessing the management card of the UPS via Web and SSH works fine and the system appears correctly configured. The documentation refers to an earlier version of the management card, but AP9631 is supposedly fully backwards compatible, and regardless of that it seems the error is on the linux box, long before it reaches the card.

I would be very grateful if someone could kindly help me point out what I have missed in order to make this work. Thank you!

grep -v "^#" apcupsd.conf |egrep -v "^\s*$"

UPSNAME SmartUPS

UPSCABLE ether

UPSTYPE pcnet

DEVICE 192.168.1.4:xxxxx:xxxx <-intentionally changed

LOCKFILE /var/lock

SCRIPTDIR /etc/apcupsd

PWRFAILDIR /etc/apcupsd

NOLOGINDIR /etc

ONBATTERYDELAY 6

BATTERYLEVEL 5

MINUTES 3

TIMEOUT 0

ANNOY 300

ANNOYDELAY 60

NOLOGON disable

KILLDELAY 0

NETSERVER on

NISIP 0.0.0.0

NISPORT 3551

EVENTSFILE /var/log/apcupsd.events

EVENTSFILEMAX 10

UPSCLASS standalone

UPSMODE disable

STATTIME 0

STATFILE /var/log/apcupsd.status

LOGSTATS off

DATATIME 0


------------------------------------------------------------------------------
Learn Graph Databases - Download FREE O'Reilly Book
"Graph Databases" is the definitive new guide to graph databases and their
applications. Written by three acclaimed leaders in the field,
this first edition is now available. Download your free book today!
http://p.sf.net/sfu/NeoTech
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users



------------------------------------------------------------------------------
Learn Graph Databases - Download FREE O'Reilly Book
"Graph Databases" is the definitive new guide to graph databases and their
applications. Written by three acclaimed leaders in the field,
this first edition is now available. Download your free book today!
http://p.sf.net/sfu/NeoTech
_______________________________________________
Apcupsd-users mailing list
[hidden email]
https://lists.sourceforge.net/lists/listinfo/apcupsd-users
Reply | Threaded
Open this post in threaded view
|  
Report Content as Inappropriate

Re: Unable to connect to UPS Network Management Card2 from CentOS

Adversio
In reply to this post by yallaone (Bugzilla)
I had the same problem, got it running using SNMP, after some more digging I finally got the pcnet protocol to work too. Seems that the password must be at least 15 characters long..